The details are correct, they are just two different models.
The SMT1500RMI2UC has 1500 VA / 1000 W output power.
The SMT1000RMI2UC has 1000 VA / 700 W output power.
The documentation with 700 W therefore refers to the smaller model SMT1000RMI2UC, not to the device offered here.
The APC Smart-UPS with model number SMT1500RMI2UC cannot be operated directly from a normal 10A household socket, taking into account the recommended electrical supply.
- The recommended electrical supply for this UPS is a 15A 120V circuit, which should be ensured via an appropriate socket or installation.
It is important to consider the specific requirements of the UPS to ensure a safe and reliable operating condition. A 10A fuse could be overloaded at full load and cause unexpected shutdown or damage.